An MCB needs to be installed in the PDU of an air-conditioner unit.
Which breaking curve should you select?

おすすめの解答:B 解答を投票する

For an MCB (Miniature Circuit Breaker) in the PDU of an air-conditioning unit, a C-Curve is recommended. C-Curve breakers are suitable for circuits with moderate inrush currents, such as those experienced in air conditioning units. They provide protection against overloads while accommodating the inrush without nuisance tripping.
Detailed Explanation:
C-Curve breakers trip when currents exceed 5 to 10 times the rated current, making them ideal for devices like air conditioners that experience moderate inrush currents upon startup. This characteristic provides a balance between protection and resilience against startup surges, preventing unnecessary trips while safeguarding the circuit.
EPI Data Center Specialist References:
EPI guidance for data center electrical systems specifies that C-Curve breakers are appropriate for equipment with inrush characteristics similar to air conditioning units, as they help prevent operational interruptions caused by typical surges during equipment start-up.